Hi,
According to NEC 501.105 B (1)
"Switches, circuit breakers, and make-andbreakcontacts of pushbuttons, relays, alarm bells, andhorns shall have enclosures identified for Class I, Division1 locations in accordance with 501.105(A)."
Does it mean that that if I have a panel located in class 1 division 2, all relays, and circuit breakers assembled inside should be approved to use in class 1 division 1?
If yes, then when we can use components certified for class 1 division 2?
Can I use electronic fuses (link below) for PLC protection and IS barrier in panel located in class 1 division 2? This electronic fuse is approved in use for class 1 division 2.
http://shop.murrelektronik.com/en/E...100600&src=search&srchPage=1&perPage=10&pos=1
According to NEC 501.105 B (1)
"Switches, circuit breakers, and make-andbreakcontacts of pushbuttons, relays, alarm bells, andhorns shall have enclosures identified for Class I, Division1 locations in accordance with 501.105(A)."
Does it mean that that if I have a panel located in class 1 division 2, all relays, and circuit breakers assembled inside should be approved to use in class 1 division 1?
If yes, then when we can use components certified for class 1 division 2?
Can I use electronic fuses (link below) for PLC protection and IS barrier in panel located in class 1 division 2? This electronic fuse is approved in use for class 1 division 2.
http://shop.murrelektronik.com/en/E...100600&src=search&srchPage=1&perPage=10&pos=1