It was a compliant install in the 60s when it was put in. I’m just wondering I’ll wait to see what my Electrical Inspector says cause the elevator inspectors really shouldn’t have any saying my disconnect he should just have from the disconnect on.
An EGC is a conductor and when 620 applies it has rules for all conductors , I am on different code cycle than you (2017) but I doubt its changed much;ya but emt can serve as a egc and is better than a wire for clearing a fault
620.11 (D) Insulation. All conductors shall have an insulation voltage
rating ...