elevator machine room
quogueelectric
new york
Wherever there is a heat detector there is a smoke detector, the smoke detector will go into alarm first 99.99% of the time and it will initiate the recall, once the heat detector trips the shunt the elevator has already been recalled.
pahlease!!!!!!!!!!!!!!!!! Do you want your mother in that elevator???? I certainly dont!99%? where are you getting your numbers from? Wrong is wrong man up and admit it. You are asking for professional help on an internet chatroom? ANY alarm should recall the elevators call Jerry Springer if you are looking for drama I will go on the show with you. (JERRY JERRY JERRY)
pgordon
Maine
ok ok im with you brother. time for me to back out of this one ....WOW sorry quogueelectric
dmanda24
this is from a document from an engineering firm
"Elevator shutdown, frequently referred to as shunt trip, is intended to immediately stop elevators before water from elevator machine room or hoistway sprinklers affects brakes and electrical equipment. Both wet brakes and wet electrical equipment can cause erratic life threatening elevator operation. Therefore, it is required by Requirement 2.8.2.3.2 of A17.1 to cause disconnection of the main line power supply upon or prior to the application of water from sprinklers in the machine room or hoistway. This occurs even if the elevator car is occupied and not at a landing. Pit sprinklers located less than 2 feet above the pit floor are exempt from this requirement because Requirement 2.8.2.3.4 of ASME A17.1 requires all electrical equipment within 4 ft of the pit floor to be NEMA 4 rated. Therefore, heat detectors or waterflow switches will typically not be required for shunt trip involving pit sprinklers. "