Elevator Motor - Full Load vs. Rated Load

Merry Christmas
Status
Not open for further replies.

Keri_WW

Senior Member
T-K sent me a spec on an a 20HP elevator (208/3) with the following information:

Total (Full Load Motor) A.C. Amps = 95 A
Rated A.C. Amps = 65.1 A
Starting A.C. Amps = 195 A.

What is the technical difference between the total (full load) amps and the rated amps as far as an elevator is concerned? I am planning on sizing my breaker at 175% of the rated amps (125A CB).

Thanks,
Keri :):)
 
T-K sent me a spec on an a 20HP elevator (208/3) with the following information:

Total (Full Load Motor) A.C. Amps = 95 A
Rated A.C. Amps = 65.1 A
Starting A.C. Amps = 195 A.

What is the technical difference between the total (full load) amps and the rated amps as far as an elevator is concerned? I am planning on sizing my breaker at 175% of the rated amps (125A CB).

Thanks,
Keri :):)

Because this is an elevator the motor is rated for duty cycle service. The conductors have to be rated for the 95 amps. See 620.13 and 430.22(E).
 
T-K sent me a spec on an a 20HP elevator (208/3) with the following information:

Total (Full Load Motor) A.C. Amps = 95 A
Rated A.C. Amps = 65.1 A
Starting A.C. Amps = 195 A.

What is the technical difference between the total (full load) amps and the rated amps as far as an elevator is concerned? I am planning on sizing my breaker at 175% of the rated amps (125A CB).

Thanks,
Keri :):)
Intermittent duty rating would be my guess.
 