I vote yes.
Interesting that the drive rated power is lower than the motor size. It’s fine given that the actual load power requirement is within the drive rating, just indicative of the elevator business being exceptionally cheap.
Now the question is, since the drive can’t deliver more than 10 HP, do you size the circuit based on that, or based on the actual motor rating (15HP)?