Elevator PITS

Status
Not open for further replies.
There is a dispute here at my shop over how many circuits are REQUIRED to be in an elevator PIT. If you respond to this thread, please read arefully 620.22, 620.23, and 620.24 before hand.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
One. Though I understand how someone might argue two. My reasoning comes from 620.24(A) and (C). (A) tells us that the lighting and receptacle(s) for the pit must be on separate circuits. But the lights don't have to be in the pit itself. If you can illuminate the pit using lights that are "above the top of the pit" (whatever that might mean), then the only circuit that serves anything "within the pit" is the receptacle circuit required by (C).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds like two circuits to me:

2017 NEC:

620.24 Branch Circuit for Hoistway Pit Lighting and Recepta‐
cles.
(A) Separate Branch Circuits. Separate branch circuits shall
supply the hoistway pit lighting and receptacles.
Required lighting shall not be connected to the load side of
a ground-fault circuit interrupter.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
One. Though I understand how someone might argue two. My reasoning comes from 620.24(A) and (C). (A) tells us that the lighting and receptacle(s) for the pit must be on separate circuits. But the lights don't have to be in the pit itself. If you can illuminate the pit using lights that are "above the top of the pit" (whatever that might mean), then the only circuit that serves anything "within the pit" is the receptacle circuit required by (C).

I don't have A17.1 handy, but I seem to recall that the light actually has to be in the pit.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
620.24 Branch Circuit for Hoistway Pit Lighting and Recepta‐
cles.
(A) Separate Branch Circuits. Separate branch circuits shall
supply the hoistway pit lighting and receptacles.
Required lighting shall not be connected to the load side of
a ground-fault circuit interrupter.

That's a change from the 2014. The 2014 required a separate circuit for the pit lighting and receptacles (that one singular circuit for both lights and recept.) While the new 2017 requires "Separate Branch Circuits" as in 2 or more circuits, apparently with the lights on one circuit and receptacles on the other circuit.

What a difference dropping an "A" and adding an "s" makes in a sentence. They should have just phrased it like 620.23(A) and said "the branch circuit supplying pit receptacles shall be separate from the branch circuit supplying pit lighting. These circuits shall supply not other loads." That would have been much clearer.

Anyhow, 2 separate circuits are required for the pit if you are under the 2017 code, and assuming you have some lighting in the pit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That's a change from the 2014. The 2014 required a separate circuit for the pit lighting and receptacles (that one singular circuit for both lights and recept.) While the new 2017 requires "Separate Branch Circuits" as in 2 or more circuits, apparently with the lights on one circuit and receptacles on the other circuit.

What a difference dropping an "A" and adding an "s" makes in a sentence. They should have just phrased it like 620.23(A) and said "the branch circuit supplying pit receptacles shall be separate from the branch circuit supplying pit lighting. These circuits shall supply not other loads." That would have been much clearer.

Anyhow, 2 separate circuits are required for the pit if you are under the 2017 code, and assuming you have some lighting in the pit.

Here's the 2014 and 2017 for comparison.

2014 NEC:

620.24 Branch Circuit for Hoistway Pit Lighting and
Receptacle(s).
(A) Separate Branch Circuit. A separate branch circuit
shall supply the hoistway pit lighting and receptacle(s).
Required lighting shall not be connected to the load
side of a ground-fault circuit interrupter.

2017 NEC:

620.24 Branch Circuit for Hoistway Pit Lighting and Recepta‐
cles.
(A) Separate Branch Circuits. Separate branch circuits shall
supply the hoistway pit lighting and receptacles.
Required lighting shall not be connected to the load side of
a ground-fault circuit interrupter.
 
I was arguing 1. Mostly because 620.23 specifically and clearly separates the receptacle circuit from the lighting circuit and 620.24 does not. If would have been ridiculously easy to just copy and paste to make them the same but kept them different. Both are titled with “separate branch circuitS”. I feel that the S is just saying that however many circuits you use, they must be separate from all other locations. Plus gfci receptacle is required in pit and it talks about the lights not coming off the load side of a gfci.
Update/FYI- the print originally called for just 1. We Wrote up an RFI and the engineer came back with a confident 1 again. Waiting on word from inspector.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO there is no argument whether or not you need separate circuits under the 2017 NEC with the code wording change. Here's the PI for the change from the 2014.

Public Input No. 457-NFPA 70-2014 [ Section No. 620.24(A) ]
(A) Separate Branch Circuit.
A separate branch circuit(s) shall supply the hoistway pit lighting and receptacle(s).
Required lighting shall not be connected to the load side of a ground-fault circuit interrupter.
Statement of Problem and Substantiation for Public Input
The requirement of the receptacle to be 120v in 620.24 (C) and the implication of section 620.24(A)that there is
only one circuit serving both lights and receptacles leads one to believe that there is only 120v lighting and
receptacle branch circuit allowed. The problem this creates is that if an inspection light or double insulated hand
tool shorts out the light in the room are out. Also in practice in larger building the lighting is 277v and a second
voltage (120v) or universal ballasts would be required for maintenance.
Allowing separate dedicated circuits for lights and separate dedicated circuit for receptacles could eliminate the
potential for injury during maintenance if the single lighting and receptacle circuit was lost due to failure of a cord
connected device.
Submitter Information Verification
Submitter Full Name Daniel Pohnert
Organization: BRPH
Street Address:
City:
State:
Zip:
Submittal Date: Wed Mar 26 16:41:54 EDT 2014
Committee Statement
Resolution: FR-3387-NFPA 70-2015
Statement: Providing separate branch circuits for lighting loads and receptacle loads will provide greater safety
for those maintaining this equipment.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I was arguing 1. Mostly because 620.23 specifically and clearly separates the receptacle circuit from the lighting circuit and 620.24 does not. If would have been ridiculously easy to just copy and paste to make them the same but kept them different. Both are titled with “separate branch circuitS”. I feel that the S is just saying that however many circuits you use, they must be separate from all other locations. Plus gfci receptacle is required in pit and it talks about the lights not coming off the load side of a gfci.
Update/FYI- the print originally called for just 1. We Wrote up an RFI and the engineer came back with a confident 1 again. Waiting on word from inspector.

Has the 2017 been adopted where you are?

I hear what you are saying about the wording, but I agree two circuits are required.

At the very least, they have made it easy for a lot of people to miss the change.
 