For sizing an elevator circuit breaker, the NEC says to size it according to article 430 which uses the full load current (FLC) motor tables.
What if the elevator motor nameplate full load amps (FLA) is larger (by about 10 A) than the table FLC?
Usually the table FLC is larger than the nameplate FLA.
What if the elevator motor nameplate full load amps (FLA) is larger (by about 10 A) than the table FLC?
Usually the table FLC is larger than the nameplate FLA.