Does an EMC/EMI filter like https://www.valinonline.com/products/508-120 go before the VFD or after the VFD on the cable that goes to the spindle? Also, if I use a filter on the output side of the VFD, would this protect both the VFD and the motor?
Or just shield them... it's a LOT less expensive!Note that for long lines from VFD to motor or with a non-inverter-rated motor you may be motivated to use a pure sine filter. That would go between the VFD and the motor, and would be a very different animal from an RFI/EMI/EMC filter which is intended to reduce unwanted high frequency components from affecting other equipment.
However, if the lines from the VFD to the motor are not shielded (either VFD cable or in metallic raceway) and are therefore able to radiate noise, you may also need to use a filter on the output side of the VFD.