We have two Cat gens supporting two different sections of the same facility, during excercise test (under load) they transfer from normal to emergency just fine. When the excercise cycle has ended and transfers back to normal, one of them (350 KVA 480V), feeder breaker (600A frame 400A trip setting) approx 190A load, trips almost everytime. The other gen 200 KW 480V approx 125 amp load acts similar except when it transfers back to normal it causes breakers on the load side to trip. These systems were installed approx a year and a half ago, they were load bank tested and fully functional tested and all worked well. Little if anything has been changed, this problem just surfaced about two weeks ago. The inphase monitors and all other pertinent features have been checked and are functional according to the Cat techs.These systems back up very important equipment in a very important facility. It has been suggested by some engineers that a breaker coordination study be done on this system. My question is if nothing has been changed and the systems were working fine what could happen to cause this problem all of a sudden. Any help finding this grimline will be greatly appreciated.
Thanks,
Wayne