K ktollar Member Jul 7, 2006 #1 Does any one know which article of the code states that for emergency circuits there should be a breakeer lock at the panel?
Does any one know which article of the code states that for emergency circuits there should be a breakeer lock at the panel?
ramdiesel3500 Senior Member Location Bloomington IN Jul 7, 2006 #2 I believe you looking for the exception at the end of rule 702.6. This is a new item in the 2005 code.
I believe you looking for the exception at the end of rule 702.6. This is a new item in the 2005 code.
steve66 Senior Member Location Illinois Occupation Engineer Jul 7, 2006 #3 700.20 might also apply, if the panelboard is in a public area, and the front cover doesn't lock. Steve
700.20 might also apply, if the panelboard is in a public area, and the front cover doesn't lock. Steve
Pierre C Belarge Senior Member Location Westchester County, New York Jul 7, 2006 #4 Are you refering to bonafide emergency circuits as per Art 700? or are you talking about possibly Art 701/702?
Are you refering to bonafide emergency circuits as per Art 700? or are you talking about possibly Art 701/702?