Emergency disconnect/ feeder disconnect

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
A building (garage apartment) approx 150’ to 130’ away from the service disconnect which feeds it, does it still require the external outside disconnect since it’s over 50’ away?

I know the code states within sight. But I thought I also read the definition of within sight is 50’.
 
A building (garage apartment) approx 150’ to 130’ away from the service disconnect which feeds it, does it still require the external outside disconnect since it’s over 50’ away?

I know the code states within sight. But I thought I also read the definition of within sight is 50’.
You would need to specific which codee applies. The 2020 only required it in a "readily accessible outdoor location"
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Are you under the 2020 NEC or the 2023 NEC?

The 2023 NEC added 225.41, which requires a feeder supplying a one or two family dwelling (units, but that word is in error and should be deleted) to have an emergency disconnect at a "readily accessible outdoor location on or within sight of the dwelling unit." And indeed "within sight" needs to be within 50', per 110.29. The 2023 NEC also has a "within sight" requirement in 230.85 for one or two family dwellings supplied by a service.

But the 2020 NEC does not have 225.41, so the requirement for emergency disconnects only applies to dwellings supplied by a service. Also, as electrofelon commented, 2020 NEC 230.85 does not have a "within sight" requirement.

Cheers, Wayne
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
So my current set up would be compliant
since I’m based on the 2020NEC

Service disconnect/emergency disconnect approx 150’ away from dwelling and going underground than stubbing up to an LB and directly into the back of a main disconnect panel.
 