I very rarely (once a year maybe) see an emergency generator - came across 1 today and have several concerns (see photos).
1. The generator is in the garage - combustion gas build-up problem plus the unit blocks access to the main disconnect.
2. One concern I have is the connections to the main breaker. The load side of the breaker (Siemans QJ22B200 - about 12 year old) is triple lugged (Problem?) - one of the cables appears to be a the "back-feed" into the system from the generator transfer switch assembly. The other services one of the panels in the home. At least one of the strands of one of the conductors are snipped to fit into the breaker.
3. Are there any rules for generator sizing? I would have expected some type of limits on the area of coverage for the generator (I usually see a standalone panel dedicated for emergency power) It appears that this generator feeds or backfeeds into the entire system (systems I have seen in the past typically only supplieds the bare essentials (heating systems, refrig. etc).
4. What would prevent the generator from back-feeding the entire grid?
Any insight would be appreciated.
http://i15.photobucket.com/albums/a352/TonyPE/100_2141.jpg
http://i15.photobucket.com/albums/a352/TonyPE/100_2140.jpg
http://i15.photobucket.com/albums/a352/TonyPE/100_2139.jpg
Regards,
Tony Shupenko, PE
1. The generator is in the garage - combustion gas build-up problem plus the unit blocks access to the main disconnect.
2. One concern I have is the connections to the main breaker. The load side of the breaker (Siemans QJ22B200 - about 12 year old) is triple lugged (Problem?) - one of the cables appears to be a the "back-feed" into the system from the generator transfer switch assembly. The other services one of the panels in the home. At least one of the strands of one of the conductors are snipped to fit into the breaker.
3. Are there any rules for generator sizing? I would have expected some type of limits on the area of coverage for the generator (I usually see a standalone panel dedicated for emergency power) It appears that this generator feeds or backfeeds into the entire system (systems I have seen in the past typically only supplieds the bare essentials (heating systems, refrig. etc).
4. What would prevent the generator from back-feeding the entire grid?
Any insight would be appreciated.
http://i15.photobucket.com/albums/a352/TonyPE/100_2141.jpg
http://i15.photobucket.com/albums/a352/TonyPE/100_2140.jpg
http://i15.photobucket.com/albums/a352/TonyPE/100_2139.jpg
Regards,
Tony Shupenko, PE