Does day rehabilitation center for adults with disabilities require emergency generator?
Sent from my SM-G935U using Tapatalk
Sent from my SM-G935U using Tapatalk
Nec 2014 is code cycle.it would take me to long to check through 2011 , 2104, 2017 for the changes based on the level of care than check the building code,
i am going to let someone working your code cycle answer that one, my thought is an egress system and most likely unit equipment would be the min. for emergency lighting
Its I-4 claasification day care facilities.Nec 2014 is code cycle.
Sent from my SM-G935U using Tapatalk
You need to know the building code adopted in that jurisdiction and review Chapter 27 and also determine if there special items or occupancies types such as fire pumps, high rise, underground, hazardous, smoke control systems, etcIts I-4 claasification day care facilities.
Sent from my SM-G935U using Tapatalk
IBC 2015 their is no chapter 27. Electrical enforces NEC 2014.You need to know the building code adopted in that jurisdiction and review Chapter 27
For example
https://codes.iccsafe.org/public/document/IBC2018/chapter-27-electrical
IBC 2015 their is no chapter 27. Electrical enforces NEC 2014.
Sent from my SM-G935U using Tapatalk
Nothing about I-4 classification.In case you need it, here is a link to the IBC 2015 Chapter 27
https://codes.iccsafe.org/public/document/IBC2015/chapter-27-electrical
Consider the other times Chapter 27 lists emergency and standy power to be required that may apply to your building for example elevators, platforms, smoke control, etcNothing about I-4 classification.