Anthony Giordano
- Oakland, NJ
Hello all, I need some assistance on what to me is a very confusing subject in the NEC. As stated above in the Title section, I need some help to properly identify how I need to move forward in a project for a client that I am currently working on.
The project is a Museum building in Long Island City, Queens, NY (NYC), is 2 Floors + a Cellar, has one (1) Elevator and no Fire Pump. We are designing an emergency generator system for our client who wants emergency power backup just for his various pump systems, namely sewage ejector pumps, dewatering pumps, etc., which are not critical building loads. The total running loads on these various pump systems if all were running at the same time would be approximately 20 kW. The emergency lighting/exit lighting is already backed up via battery packs and a Lighting Inverter System, so he does not want these lighting loads on our generator. He also does not want the elevator on generator power.
After coordinating with our generator vendor, the sizing program came back with two sizes...a 53 kw and 80kw emergency generator. For cost purposes, we were asked to use the 53 kW Genset in our base design, but I am going to also provide an alternate design using the 80kw Genset to present to the client. My approach to the design is to have one ATS (either 200A or 400A, for each option), which will receive the emergency feeder from the generator and the normal feeder from a C/B in the building's 2000A, 208V, 3-phase, 4-wire MDP. The load side of the ATS would then in turn feed a new DP, which will feed our loads.
The building is not a Health Care facility, therefore NEC Article 517 does not apply. Are there any code implications or limitations in Articles 700, 701, 702 or 710 that I need to be aware of that would play a role in not permitting me to approach the design as stated above? Please chime in with any thoughts or comments, thanks!
A.G.
A.G.