Attached i have emergency generator in high rise building.
The emergency generator has two main breaker one 150A which goes to fire pump 480V three phase and another 600A which goes to distribution Panel Gen
Panel Gen demand load is 120.28A at 480V three phase and 100kVA.
The emergency generator total demand load including fire pump and Gen is 292.71A at 480/277V three phase and demand of 243.5kvA.
Generator capacity is 400kw at 480V three phase is 481.13A.
The emergency generator at present has enough capacity. One can add in future and i think emergency generator maybe undersized for that. So the breaker 150A + 600A = 750A would be the total load while generator demand capacity is 481Ax1.25=601A.
Questions:
1. Would the generator capacity be full load amps of the generator or generator FLAx1.25?
2. Is their anything in the NEC 2017 that address future loads of the generator capacity must also be enough to support its load when sizing emergency generator? I know load shedding but can that be also for future and can be enforced now Not in future?
3. Panel Gen total demand load is 120.28A while the breaker provided is 600A? Is there anything in NEC 2017 that limits the size of emergency breaker?
4. Optional loads demand loads are 133A yet breaker provided is 200A. Is this breaker sized correct? Is there anything in NEC 2017 which says how to size that breaker?
5. Life and safety total loads are 131.9A but breaker provided is 225A. Is this breaker size correct? Is their anything in NEC 2017 which says how to size the breaker?
The emergency generator has two main breaker one 150A which goes to fire pump 480V three phase and another 600A which goes to distribution Panel Gen
Panel Gen demand load is 120.28A at 480V three phase and 100kVA.
The emergency generator total demand load including fire pump and Gen is 292.71A at 480/277V three phase and demand of 243.5kvA.
Generator capacity is 400kw at 480V three phase is 481.13A.
The emergency generator at present has enough capacity. One can add in future and i think emergency generator maybe undersized for that. So the breaker 150A + 600A = 750A would be the total load while generator demand capacity is 481Ax1.25=601A.
Questions:
1. Would the generator capacity be full load amps of the generator or generator FLAx1.25?
2. Is their anything in the NEC 2017 that address future loads of the generator capacity must also be enough to support its load when sizing emergency generator? I know load shedding but can that be also for future and can be enforced now Not in future?
3. Panel Gen total demand load is 120.28A while the breaker provided is 600A? Is there anything in NEC 2017 that limits the size of emergency breaker?
4. Optional loads demand loads are 133A yet breaker provided is 200A. Is this breaker sized correct? Is there anything in NEC 2017 which says how to size that breaker?
5. Life and safety total loads are 131.9A but breaker provided is 225A. Is this breaker size correct? Is their anything in NEC 2017 which says how to size the breaker?