Emergency Lighting 2 X 2 troffers

Status
Not open for further replies.

jiml

Member
Are company is in the process of changing out 2 X 2 lights with LED. The old emergency 2 X 2 lights come with a test switch, the new LED's do not. Does the code require a test switch on the 2 X 2 LED emergency lights. If so, can the test switch be above the drop ceiling?

Thank you,
Jim
CT.
 

mgookin

Senior Member
Location
Fort Myers, FL
Are company is in the process of changing out 2 X 2 lights with LED. The old emergency 2 X 2 lights come with a test switch, the new LED's do not. Does the code require a test switch on the 2 X 2 LED emergency lights. If so, can the test switch be above the drop ceiling?

Thank you,
Jim
CT.

Welcome back to the forums!

It sounds interesting that you're buying new emergency lights that don't have a test switch. My opinion is yes, they have to be testable. As to convenience of test switch location, I don't know off the top of my head how accessible that must be.
 

LEO2854

Esteemed Member
Location
Ma
Are company is in the process of changing out 2 X 2 lights with LED. The old emergency 2 X 2 lights come with a test switch, the new LED's do not. Does the code require a test switch on the 2 X 2 LED emergency lights. If so, can the test switch be above the drop ceiling?

Thank you,
Jim
CT.

I don't think it's required by the NEC,But this could be a local code rule.

Also Welcome back to the forum.:)
 

sullivant

Member
Location
Holyoke, MA USA
"Readily Accessible"

"Readily Accessible"

Welcome back to the forums!

It sounds interesting that you're buying new emergency lights that don't have a test switch. My opinion is yes, they have to be testable. As to convenience of test switch location, I don't know off the top of my head how accessible that must be.

Testing components for Life Safety is required to be readily accessible. In as such, it must be mounted where it can be accessed without removing any building structure.
 

cadpoint

Senior Member
Location
Durham, NC
Well, if it does not have a test switch does it even have a battery backup inside?

Is this light circuit inline with other lights or does it have it's own circuit?
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Well, if it does not have a test switch does it even have a battery backup inside?

Is this light circuit inline with other lights or does it have it's own circuit?

That was my first though too!!

Do any of the new LED lights have a battery backup??
 