Emergency Lighting Circuits

Status
Not open for further replies.

fester

Member
I am installing self contained battery back-up emergency lighting units. I can't quite tell by looking in the code book if the 120v circuit that feeds these units must be in a separate conduit, or can the feed be tapped off of the general lighting circuit. Section 700.9 (B) is unclear to me. Thanks
 
Re: Emergency Lighting Circuits

I'm not following your question...if the units are self contained, how else could the feeds enter other than through a seperate means. Generally speaking, self contained emer. lighting is tapped off the line side of any switches serving the area to be illuminated by the self contained emer. lights.
 
Re: Emergency Lighting Circuits

...the handbook even has a picture of one :p in 700.12(E). Nice call kturner !

[ March 30, 2005, 02:10 PM: Message edited by: celtic ]
 
Re: Emergency Lighting Circuits

My apologies for not asking the right question, I should have rephrased what I was asking. I was more concerned with the actual conductors that feed the emergency light units themselves. Can these conductors be in the same raceway as the conductors that feed the general lighting or must I run a separate conduit just for the emergency lighting conductors. I have a contactor back at the main panel board for switching of the general lighting.I understand that the connection point for the emergency lighting circuit will be on the line side of any switching device. Thanks again
 
Re: Emergency Lighting Circuits

Fester the line voltage conductors feeding an emergency battery unit are not part of the emergency system.

The emergency system in this case starts at the emergency battery unit.

If you feed remote low volt lighting fixtures from these battery units those conductors would be part of the emergency system and would have to be separate.
 
Re: Emergency Lighting Circuits

Originally posted by fester:
...Can these conductors be in the same raceway as the conductors that feed the general lighting or must I run a separate conduit just for the emergency lighting conductors. I have a contactor back at the main panel board for switching of the general lighting.
700.9(B)
No, they cannot be in the same raceway, cable, box, or cabinet with the regular or normal wiring. the in and outs are all explained in 700.9(B) 1 through 4.
 
Re: Emergency Lighting Circuits

Originally posted by celtic:
Originally posted by fester:
...Can these conductors be in the same raceway as the conductors that feed the general lighting or must I run a separate conduit just for the emergency lighting conductors. I have a contactor back at the main panel board for switching of the general lighting.
700.9(B)
No, they cannot be in the same raceway, cable, box, or cabinet with the regular or normal wiring. the in and outs are all explained in 700.9(B) 1 through 4.
Celtic we are taking about the supply conductors to battery equipment.

They are not emergency system conductors.

If we were to say they where emergency system conductors how far back would they have to remain separate?

Back to the sub panel?

Back to the service panel?

Back to the utility?
 
Re: Emergency Lighting Circuits

If an area has 1 or 2 branch circuits units battery emergency lights MUST be connected to the lighting circuits. For 3 or more lighting circuits the unit battery emergency lights MUST be connected to the same panelboard. Otherwise, the battery units would not kick on if there is a power failure particularly a branch circuit breaker tripping out.
 
Re: Emergency Lighting Circuits

MC, that had eveything but the reference to back up your statement. :D

Free of charge: 700.12(F).

Edit:
Originally posted by infinity:
Don't you mean 700.12(F)?
Oops. :D

[ March 31, 2005, 06:55 AM: Message edited by: georgestolz ]
 
Re: Emergency Lighting Circuits

mc5w,
For 3 or more lighting circuits the unit battery emergency lights MUST be connected to the same panelboard.
I don't think so. The exception says that where the area is served by 3 or more lighting circuits from the same panel, then an additional circuit from that same panel shall be permitted to supply the unit lighting equipment.
Don

[ March 31, 2005, 07:42 AM: Message edited by: don_resqcapt19 ]
 
Re: Emergency Lighting Circuits

fester,if you are asking if you can pull both an unswitched hot to serve the EM fixture and the switched conductors in the same home run conduit the answer is yes. These are all normal power conductors;the only emergency power conductors are inside the EM fixture. See 700.12(E) NEC 2002. (I don't have 2005 yet).
 
Re: Emergency Lighting Circuits

Thank you kturner, that was the info I was looking for. I did not want to cause so much discussion about this topic. I certainly appreciate all of the feedback from everybody. It is good to see the vast wealth of knowledge that is available to anyone. Thanks again.
 
Re: Emergency Lighting Circuits

Originally posted by iwire:

They are not emergency system conductors.
I stand corrected...not sure what I was thinking..my apologizes for misinformation.(700.9)
 