Emergency lighting ckt

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
For emergency exit lighting in an apartment or business (exit sign above door). I was under the impression that it was required that you hook the emergency exit light to the lighting circuit to that area. I could not find the code reference I would appreciate help getting in the area of the NEC for this situation. In 700 i seen some info but I think that was more related to entire systems not the typical bug eye over the door with a battery inside.
 
700.12(F)

unit equipment

2020 revised this
Thanks It looks like 700.12(I)(2)(3)a&b hit the nail on the head in NFPA link 2020 version. I don't know why the unit equipment threw me off. Thanks again.
 