Re: Emergency Lighting Load for Generator Sizing
I agree the BEST way to do this is to meter the lighting however the building is over 100 years old so who knows if the lighting is fed from a one panelboard or multiple panelboards. Plus, there is no em ltg on the 5th and 6th floors so metering will not help you there. The metering of the other floors would give you a base va/sf, but who knows what the em ltg was designed to on that floor. The original question is what is typical va/sf that is used to size the em ltg load for a generator when the lighting is not known. Sometimes the best way of doing things is not always practical or can be time consuming and you must use good engineering figures, such as the .5va/sf. which would give you a good ballpark load for the lighting.
I also agree the va/sf number will change based upon what you are lighting for , i.e. em egress ltg or normal bldg operation. but the question that was asked, that we have gotten away from, is what is a typical va/sf for em ltg when sizing a generator when the lighting is not known.
[ April 21, 2004, 09:52 AM: Message edited by: bwyllie ]