Re: Emergency Lighting Load for Generator Sizing

For pre-1975 high rises in chicago, you only need em power for the Emergency Lighting. On this particular job, the only way to figure what the lighting load would be, is to get floor plans for every floor and lay it out. There are not floor plans available. The emergency lighting is not all currently fed from the existing em ltg panelboard. They have taken out the em ltg on two floors and replaced it with battery packs. So an amp draw or fixture count will not give me an adequate connected load either. The generator size that we are putting in, is more power than the existing em ltg panelboard is rated for, by quite a bit actually. The reason I asked the question, is that the owner wants to do the job for $12,000. The way we designed it was about $50,000 if I remember the quote correctly. But the $12,000 number was given to him by a contractor who had proposed a much smaller generator. He had also proposed feeding the existing 208v single phase em service with a 240v single phase generator. But all the owner thinks about is the initial quote of $12,000 and how much cheaper it is than reality. So I asked the question of what other people use for a VA/SF basis to size generators based on previous experience. Even for new jobs you can use a VA/SF to get started and then massage it to what actually ends up being connected as the design progresses. That is why it is a useful number.
 
Re: Emergency Lighting Load for Generator Sizing

I work in Chicago too. Wouldnt you use the values given in 18-27-220.3a for halls ,corridors,closets and stairways?
 
Re: Emergency Lighting Load for Generator Sizing

Its 18-27-700.12. Only .1 va per sq ft. required for em. lighting systems here in Chicago. But your probably way ahead of me.
 
Re: Emergency Lighting Load for Generator Sizing

Justin,
the 0.1 watts/sf is a code minimum. I already have more than that connected without the 5th and 6th floor. That number is too low in my experience. That is why I want to find what other engineers are using. Thanks for trying to help. Good to see someone else has to suffer with the chicago code. It sure would have been nice if they would have somehow highlighted where they made changes or additions/deletions to the 1999 NEC. Justin, make sure you check out the code changes that are only listed on the web site, even tho, they were made a couple years ago and the 2004 edition says it includes everything up until a time after those were posted. Especially if you are doing generator retrofits.
 
Re: Emergency Lighting Load for Generator Sizing

Originally posted by justin7:
I work in Chicago too. Wouldnt you use the values given in 18-27-220.3a for halls ,corridors,closets and stairways?
those are the values for full lighting. EM lighting only needs to be 1 foot candle.
 