Re: emergency lights in a restaurant
(c) Unit Battery Equipment.
(1) All unit batteries shall be labeled as emergency lighting equipment. Individual unit equipment for code required standby
emergency illumination shall consist of the following:
(a) A rechargeable battery;
(b) A battery charging means;
(c) Provisions for one or more lamps;
(d) A relaying device arranged to automatically energize the lamps upon failure of the supply to the unit equipment;
(e) Batteries of suitable rating and capacity to supply and maintain not less than 87? percent of the nominal battery voltage for
the total lamp load associated with the unit for a period of at least 1? hours; and
(f) Acid or alkali storage batteries designed and constructed to meet the requirements of emergency service.
(2) The unit equipment shall be provided with:
(a) A test switch for checking the operating conditions of the unit;
(b) A pilot light to indicate current supply from the normal source; and
(c) A pilot light or meter to indicate the battery is charging. Where a common pilot light is used it shall have a distinctive
difference in illumination to indicate the normal charging rate and the float charging rate. It is not permitted for this pilot
light to be marked "READY" to indicate power available.
(3) Enclosure. The unit battery enclosure and lamp holder shall be made of metal. Plastic enclosures are not acceptable.
(4) Wiring.
(a) The wiring shall comply with the following:
(1) Unit equipment shall be permanently fixed in place and supplied with an approved metallic raceway;(2) Flexible cord and plug connections shall not be permitted;
(3) The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal illumination, or
(emergency illumination where present) in the area and connected ahead of any local switches;
(4) The branch-circuit device shall be a type S plug fuse, a circuit breaker of the key operated type, or shall be provided with a
locking device to prevent inadvertent opening of the circuit and shall comply with Section 18-27-700.63;
(5) The panel directory shall be prominently marked to identify the circuits that supply the unit batteries.
(6) Where there is a separate and uninterrupted area supplied by a minimum of 3 normal lighting circuits, a separate branch circuit
for unit batteries shall be permitted, provided the circuit originates from the same panelboard as that of the normal lighting
circuits and is either a type S plug fuse, a circuit breaker of the key-operated type, or a circuit breaker provided with a lock-on
feature.