Emergency lights

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
My question is can I put the emergency ights on a regular light circuit? This is commercial and I don’t have my code book with me .
 
My question is can I put the emergency ights on a regular light circuit? This is commercial and I don’t have my code book with me .

If these are battery backup e-lights the answer is not only "yes you can" but also "yes you should". The e-lights should share the same circuit as the lights providing regular illumination. That way, if the circuit goes down for reasons other than a general building blackout, occupants can exit the affected area safely.
 
If you are installing EBU’s, these have to be on the same circuit that serves the lights in the area where you are installing the EBU's
And they may need a separate source of constant power so that they can distinguish between a power failure and someone turning off the lights at a switch. (If the fixtures are not always-on night lights they would have to turn on in the case of an actual power failure.)
 
And they may need a separate source of constant power so that they can distinguish between a power failure and someone turning off the lights at a switch. (If the fixtures are not always-on night lights they would have to turn on in the case of an actual power failure.)
Not really a "separate source" but an unswitched source from the same circuit that supplies the normal lighting in the area.
 