Our firm is providing electrical engineering services for design of a county office building which contains many of the county offices including an Emergency Operations Center (EOC). The building is single story therefore no elevators and there is no fire pump. We are designing a standby power system for the EOC and I am trying to get my head around classifying the loads for the operation. I have read many threads concerning Articles 700, 701 and 702 but there is one point that I want to clarify. I am classifying the loads roughly as follows:
Article 700 Loads - Emergency and exit lighting, fire alarm and possibly communications systems.
Article 701 Loads - All other loads required for the EOC to perform its function.
Part of my interpretation of Article 700 loads is this: Article 700 loads pertain to life safety and health hazards only to the building occupants. It has nothing to do with the function even if it is for some kind of emergency services.
Is this interpretation correct?
One of our strategies, to avoid having to have two transfer switches and separate distribution, is to provide the required battery back up for all of the Article 700 loads in the building including the EOC. The Standby Power System is dedicated only to the EOC.
Article 700 Loads - Emergency and exit lighting, fire alarm and possibly communications systems.
Article 701 Loads - All other loads required for the EOC to perform its function.
Part of my interpretation of Article 700 loads is this: Article 700 loads pertain to life safety and health hazards only to the building occupants. It has nothing to do with the function even if it is for some kind of emergency services.
Is this interpretation correct?
One of our strategies, to avoid having to have two transfer switches and separate distribution, is to provide the required battery back up for all of the Article 700 loads in the building including the EOC. The Standby Power System is dedicated only to the EOC.