We are installing a 800 amp emergency generator with main breaker in Generator.
This feeder runs into the building stubbed into electrical room #1, then ran approximately 35' from Electrical room #1 to Electr4ical room #2 to the Generator panel (GDP). From GDP, to other panels (Life Safety, Critical branch panel, Equipment branch).
Electrical room #1 = main electrical switch gear.
Electrical room #2 = Where the Emergency panel located.
The electrical engineer is stating that the feeders from the generator needs to follow the 15' rule, like unfused conductors rule. Is this true?
Also, the engineer is stating that Data cabling are not allowed in the electrical room #1. Is this true?
The reason we are stubbing into Electrical room #1, is because Electrical room #2 would put us 15' below grade. Just in case you were wondering.