L lisat Member Jan 20, 2009 #1 I'm working on a project where they are looking at making a school an emergency shelter, just wondering if anyone has any information on how long the generator should run for this?
I'm working on a project where they are looking at making a school an emergency shelter, just wondering if anyone has any information on how long the generator should run for this?
ron Senior Member Location New York, 40.7514,-73.9925 Jan 20, 2009 #2 2 hours of full demand operation of the system minimum per 700.12(B)(2). Many voluntarily go past that to 1-2 days.
2 hours of full demand operation of the system minimum per 700.12(B)(2). Many voluntarily go past that to 1-2 days.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 21, 2009 #3 The guidelines for the emergency services when planning for a major disaster is that you have to be self sufficient for the first 72 hours.
The guidelines for the emergency services when planning for a major disaster is that you have to be self sufficient for the first 72 hours.
ron Senior Member Location New York, 40.7514,-73.9925 Jan 21, 2009 #4 Don has a point, although I didn't think a school would be a designated critical operations area per Article 708, but I guess it is worth asking.
Don has a point, although I didn't think a school would be a designated critical operations area per Article 708, but I guess it is worth asking.