451F
The site is a fleet diesel dispensing system. The owner wants maximum redundancy to avoid shut down of the entire system.
The installation is two suction pump dispensers with internal 2' fluorescent lights. The pumps are controlled by a Ward controller that is monitored remotely by a computer. The Ward is outside of the classified area.
The dispenser manufacturer wants the lights on separate circuits from the pumps.
Two questions:
1. Is there an industry standard method of wiring?
2. My thoughts are these, what do you think?
a. Three switched-neutral shunt-trip breakers
i. one for each dispenser
ii. one for the lights in both dispensers
b. Momentary contact emergency shut off (ESO) mushroom switch with plastic shield (STI stopper station)
c. Feed 120v to ESO from dedicated breaker equipped with a toggle-lock
d. daisy chain shunt-trips to ESO using wire nuts to permit quick replacement of breakers
e. separate neutrals to shunt-trips
TG
Two questions:
TG