D djd Senior Member Aug 29, 2020 #1 I am just wondering how that would be done if the service is in a locked outdoor closet , shunt trip on the main breaker.
I am just wondering how that would be done if the service is in a locked outdoor closet , shunt trip on the main breaker.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Aug 29, 2020 #3 Fire dept have bolt cutters. For an external disconnect I would expect the disconnect cover to be locked
Fire dept have bolt cutters. For an external disconnect I would expect the disconnect cover to be locked
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 30, 2020 #4 djd said: I am just wondering how that would be done if the service is in a locked outdoor closet , shunt trip on the main breaker. Click to expand... I would not accept that as being "outside".
djd said: I am just wondering how that would be done if the service is in a locked outdoor closet , shunt trip on the main breaker. Click to expand... I would not accept that as being "outside".