Hi all.
I was asked my opinion today on the following scenario.
Building #1 - Nursing Home building. Has a backup generator.
Building #2 - New small building. Owner wants it to have its own service. It will have a pre-action fire suppression system with a compressor as well as loads considered to be "emergency" or on legally required standby systems. I am not sure which (not my project, this was an acquaintance asking me this). The Owner does not want to install a transfer switch or switches in the new building but instead just wants to extend branch circuits or feeder(s) from Building #1. Owner says this is legal and "they've done it before" at other buildings.
I told the acquaintance that branch circuits or feeders from another building are not allowable sources for Art. 700 or 701 loads even if the Building #1 source is generator backed.
Correct or no?
Thanks.
I was asked my opinion today on the following scenario.
Building #1 - Nursing Home building. Has a backup generator.
Building #2 - New small building. Owner wants it to have its own service. It will have a pre-action fire suppression system with a compressor as well as loads considered to be "emergency" or on legally required standby systems. I am not sure which (not my project, this was an acquaintance asking me this). The Owner does not want to install a transfer switch or switches in the new building but instead just wants to extend branch circuits or feeder(s) from Building #1. Owner says this is legal and "they've done it before" at other buildings.