I am designing a new lab building. It will have its own generator, with separate Emergency (egress lights only) and Optional Standby Systems.
An existing, adjacent lab building has one small lab space that has its own small (12 kW) generator. The generator's output is connected to an ATS, then to a UPS, then to a branch circuit panel, all of which is inside the lab. The generator is located just outside the loading dock between the new lab building and the existing lab building. It is presently treated as Optional Standby. It?s in our way, so it has to be relocated, replaced, or otherwise reconfigured. We are discussing placing this existing load on our new generator.
The lab served by this small generator performs a vital role in the monitoring of seismic activity. For that reason, if we put that load on our new generator, the owner wants it powered by our Emergency ATS. I want to talk the owner out of that, and I would to be able to use some basis other than the fact that the loss of power to this lab would not, by itself, put anyone?s life or safety at risk.
Here is my question: I know that if we supply this load from our Emergency ATS, that will bring into play some rules regarding the feeder from our building to theirs. But will it also require the lab to upgrade its internal wiring, to meet the required wiring methods for emergency systems?
An existing, adjacent lab building has one small lab space that has its own small (12 kW) generator. The generator's output is connected to an ATS, then to a UPS, then to a branch circuit panel, all of which is inside the lab. The generator is located just outside the loading dock between the new lab building and the existing lab building. It is presently treated as Optional Standby. It?s in our way, so it has to be relocated, replaced, or otherwise reconfigured. We are discussing placing this existing load on our new generator.
The lab served by this small generator performs a vital role in the monitoring of seismic activity. For that reason, if we put that load on our new generator, the owner wants it powered by our Emergency ATS. I want to talk the owner out of that, and I would to be able to use some basis other than the fact that the loss of power to this lab would not, by itself, put anyone?s life or safety at risk.
Here is my question: I know that if we supply this load from our Emergency ATS, that will bring into play some rules regarding the feeder from our building to theirs. But will it also require the lab to upgrade its internal wiring, to meet the required wiring methods for emergency systems?