I'm designing a new facility (airport terminal) in which there are 700, 701, and 702 loads. The generator is located outside the terminal. According to the NEC 2005 handbook section 700.9 (blue print) I can run one feeder from the genererator into the building and terminate it in a switchboard (not a panelboard). From the switchboard I can then go out to my three seperate transfer switches and there corresponding panelboards. My questions are:
A) Can the switchboard, all three transfer switches, and the panelboards all be located in the same room. (It is a seperate room away from the normal service electrical room.)
B) What should the fire rating of the room be? Arcticle 700.12 states minimum of 1 hour. NFPA 110 section 7.2.1.1 states 2 hours although this is when the generator itself is within the room.
I have asked numerous others and I have recieved numerous answers. Just hoping for some opinions!!
Thanks
BG
A) Can the switchboard, all three transfer switches, and the panelboards all be located in the same room. (It is a seperate room away from the normal service electrical room.)
B) What should the fire rating of the room be? Arcticle 700.12 states minimum of 1 hour. NFPA 110 section 7.2.1.1 states 2 hours although this is when the generator itself is within the room.
I have asked numerous others and I have recieved numerous answers. Just hoping for some opinions!!
Thanks
BG