I agree with Steve66 and Jim. This issue came up at our new NBA arena. I interpreted the code the same way Iwire did. I called NFPA and got their opinion. A single feeder from the generator is permitted to supply a switchboard or panelboard and then branch off to the different classes of loads. The emergency system does not begin until the feeder leaves this distribution point. From that point on it must be separate from normal power except at the transfer switch. As Jim said "Emergency source distribution" is the key here.
I agree with Steve66 and Jim. This issue came up at our new NBA arena. I interpreted the code the same way Iwire did. I called NFPA and got their opinion. A single feeder from the generator is permitted to supply a switchboard or panelboard and then branch off to the different classes of loads. The emergency system does not begin until the feeder leaves this distribution point. From that point on it must be separate from normal power except at the transfer switch. As Jim said "Emergency source distribution" is the key here.