I have a case where I need to run EMT along the solar aluminum rails. Instead of using separate conduit supports, I can attach EMT to aluminum rail via stainless steel hooks bolted to rails, as shown in the image below. Do you see a problem with this arrangement?
Enclosure is bolted to the aluminum rail with stainless steel bolts. Enclosure is also aluminium.
Use of stainless fittings to attach EMT to Al rails is necessary to avoid electrolytic corrosion if steel EMT is used. If you use galvanized pipe then direct contact may be OK.