Are these bulletins valid?
https://www.nema.org/Technical/Documents/Steel Conduit and EMT-Proven to Meet the NEC Reg.pdf
https://www.google.com/url?sa=t&rct...08-20-08.ppt&usg=AOvVaw3PjNAeADwoNOWWbSRJA3l3
Basically that are saying that over 300-400 feet of conduit run you no longer have an effective fault current path. However code makes no mention of this, and some installations would automatically be in violation.
Also does the code saying anything about up sizing EMT/GRC/ect when the current carrying conductors are up-sized for voltage drop prided fill has not been exceeded?
https://www.nema.org/Technical/Documents/Steel Conduit and EMT-Proven to Meet the NEC Reg.pdf
https://www.google.com/url?sa=t&rct...08-20-08.ppt&usg=AOvVaw3PjNAeADwoNOWWbSRJA3l3
Basically that are saying that over 300-400 feet of conduit run you no longer have an effective fault current path. However code makes no mention of this, and some installations would automatically be in violation.
Also does the code saying anything about up sizing EMT/GRC/ect when the current carrying conductors are up-sized for voltage drop prided fill has not been exceeded?