Another C10
Electrical Contractor 1987 - present
- Location
- Southern Cal
- Occupation
- Electrician NEC 2020
What you describe is called skin effect. At 60Hz it is negligible for conductor sizes to about 250kCMIL. At 750kCMIL the multiplier is only around 1.2, this is why we pretty much ignore skin effect for most building circuits.Well .. from what I've understood in the past, for one thing the fault current would run on the surface of the conduit not through it, that's just the nature of electricity, with that said I've heard that some conductors probably major utility power lines have at times been basically hollow tubing, because just like a conductor the circular mils of the diameter is what determines the current flow ease.
I was taught 30+ years ago which seemed reasonable and at the same time amazing that current flow, voltage etc .. does not necessarily move from molecule to molecule throughout the entire conductor, it was expressed that, not like water in a hose electricity actually travels on the surface or skin of the object therefor the rest of the conductor is basically useless, the outer diameter of the conductor (circular mils ) aka gauge establishes the safe surface area necessary for transporting specific demands of energy.we pretty much ignore skin effect for most building circuits.
Yes, but the current 'penetration depth' at 60hz is fairly large, and is taken into account in NEC tables. You need to exceed 1000kcmil before you would even consider hollow conductors. Skin effect is more pronounced in rectangular conductors like bus bar, particularly when they are paralleled for large currents. Skin effect is not an issue for tubular conductors with relatively thin walls, like are used in open air substations or conduit used as a grounding conductor.I was taught 30+ years ago which seemed reasonable and at the same time amazing that current flow, voltage etc .. does not necessarily move from molecule to molecule throughout the entire conductor, it was expressed that, not like water in a hose electricity actually travels on the surface or skin of the object therefor the rest of the conductor is basically useless, the outer diameter of the conductor (circular mils ) aka gauge establishes the safe surface area necessary for transporting specific demands of energy.
Back in high school, I was in the Radio Club, and one of our field trips was to a local TV station. The main transmission line, which we saw, was, we were told, made of 1" copper pipe and soldered fittings inside 3" copper pipe and soldered fittings (I'm not 100% sure of the sizes) with nylon blocks to maintain centering. The visible parts, and the soldering, looked just like standard plumbing pipe and fittings.For RF use (coax and antennas and the like), skin effect is huge.
I may be misunderstanding your valuable input, when I mention skin or surface travel, I'm simply relaying what I was taught about how electricity travels on a conductor, granted I only know what I've learned or how I was taught but it sounds like your mentioning that aside from on the skin of a conductive material, also some depth is included, which is interesting in it self, I remember my ol wise instructor mentioning, " If you could measure the inside of an energized conductor there would be no voltage" obviously the whole class of young minds were very doubtful but he seemed pretty persistent on his past learning and research and pushed it to us, He said " Electricity flows on the outer surface of objects" which is why today I explained what I believe to everyone here, am I right, ..I'd like to think so. If not well fortunately I have a great classroom right here.Almost every electrician I know has been taught skin effect as something that needs to be considered, but most 'power' engineers I know have never dealt with it.
Skin effect virtually never impacts the work of most inside electricians.
It might barely be an issue for large 400Hz installations.
It certainly is an issue for large scale power distribution.
For RF use (coax and antennas and the like), skin effect is huge.
-Jon
He said " Electricity flows on the outer surface of objects" which is why today I explained what I believe to everyone here, am I right, ..I'd like to think so. If not well fortunately I have a great classroom right here.
This phenomenon is called the skin effect, and it is caused by the changing magnetic field within the conductor causing a repulsion of the moving electrons from the center of the conductor. The effect is frequency dependent, and at 60Hz can be ignored except for very large diameter conductors. And even then it is only a few percent difference in resistance between AC and DC.Well .. from what I've understood in the past, for one thing the fault current would run on the surface of the conduit not through it, that's just the nature of electricity, with that said I've heard that some conductors probably major utility power lines have at times been basically hollow tubing, because just like a conductor the circular mils of the diameter is what determines the current flow ease.
Your teacher was wrong. Sounding plausible, but wrong.I may be misunderstanding your valuable input, when I mention skin or surface travel, I'm simply relaying what I was taught about how electricity travels on a conductor, granted I only know what I've learned or how I was taught but it sounds like your mentioning that aside from on the skin of a conductive material, also some depth is included, which is interesting in it self, I remember my ol wise instructor mentioning, " If you could measure the inside of an energized conductor there would be no voltage" obviously the whole class of young minds were very doubtful but he seemed pretty persistent on his past learning and research and pushed it to us, He said " Electricity flows on the outer surface of objects" which is why today I explained what I believe to everyone here, am I right, ..I'd like to think so. If not well fortunately I have a great classroom right here.
Thanks folks for sharing your wisdom and lessons so freely.
The cost is the same, lager ID = more fill, lighter weight. But it is a tougher steel, harder to thread and bend.I have heard that it is a different alloy and is harder to thread and bend despite having thinner wall. I have used it a few times but never threaded or bent it.
Now out of respect for a person I though and still do think was a pretty intelligent educator of electricity, granted products get upgraded and theories turn more into facts based on further research studies.Your teacher was wrong. Sounding plausible, but wrong.
If still same CSA you still have same amount of copper. If flattened out you have more surface area, but less "depth".Now out of respect for a person I though and still do think was a pretty intelligent educator of electricity, granted products get upgraded and theories turn more into facts based on further research studies.
This is a product that to me contradicts the depth theory involved upon a conductor regarding current flow and its nature. I'm just posting this for your input regarding the concept were in this case a 20 A current flow can travel on a paper thin conductor. the diameter is not the concern in this design but notice the circular mills are basically transformed or translated into a wide flat mass. seems pretty Interesting ..
View attachment 2552844
If you want to waste money and natural resources then that is one of the best ways to do it..... Where distance becomes an issue though, do you just run a grounding conductor sized for the largest circuit in the raceway?