emt conduit installation
sunshine
the installation of 40 feet EMT conduit with 3 each -2 AWG THHN, 4 each-6 AWG THHN and 3 each -10AWG THHN conductors . what is the minimum conduit size. Thanks Bill
Code:
Re: emt conduit installation
Bill, just for fun, go to chapter 9 and try to figure it yourself.
Might this be an exam question? :)
Roger
Bill, after rereading my reply, it doesn't come across the way I meant it. :(
Do the calculations and post your conclusion here for a verification or correction.
Roger
[ January 21, 2005, 10:41 PM: Message edited by: roger ]
I hope I don?t step on any toes. I thought I would give a stab at this. It has been a while since I have done this. This is for my own edification.
Table 5, Chapter 9
3-- # 2 THHN @ .1158 = .3474 in2
4-- # 6 THHN @ .0507 = .2028 in2
3-- # 10 THHN @ .0211 = .0633 in2
I come up with .6135 in2
Table 4, Chapter 9
Over 2 @ 40% -- 1 1/2 EMT @ .814 in2
I would like to take this one step further, what about ?derating? (adjustment factor, Table 310.15(B)(2)(a)) for this situation? I would think without knowing the # of Current Carrying Conductors we could not get a good answer. Is this correct?
Norb
Norb
yes, but why would anyone run conductors that big if they carried no current?
Bob many times the NEC does not count the neutral as a current carrying conductor for the purposes of derating.
We do not know from the opening post if all the conductors are current carrying or not.
Check out 310.15(B)(4)(a),(b) & (c).
I guess if I looked closer and figured on only one of the # 10's was a neutral, not counted per 310.15(B)(4)(a), we would use a count of 7-9 @ 70%. What might I be missing?
Norb
[ January 23, 2005, 10:01 AM: Message edited by: 1793 ]
Norb, you are correct, and as far as an exam, the question couldn't be answered for derating of conductors, only conduit fill.
Roger
to the conduit fill question 3#2thhn ,4#6thhn and3#10thhn copper conductors,supplied from a braker having 75degree C,termination #6 thhn=0.0507x3=0.1521 . #2thhn=0.01158x2=0.2316 #10thhn=0.0211x3=0.0633 The total=0.447sqinch table 4 chapter 9 EMT conduit at40% fill=0.447=0.598sq inch Table 4 shows 1.25 EMT CONDUIT. Did i miss anything? thanks Bill
You only counted (2) #2's. Why not (3)??
If this is a test question, and that was the only given info, I would count All of them for the answer.
to the question of the conduit fill:3#6 thhn=0.2028, 3#2thhn=0.3474. and 3#10thhn=0.0633.the total of 0.6135 with 40%fill table 4 EMT conduit =1.5 size,is this correct? thanks Bill
For THHN insulated wire (3)#10 , (4)#6, (3)#2 in EMT conduit I would recommend using 1-1/2" size.
David ;)
Bill, you are correct for the tubing size, but you need to look at the #6 again. .
Roger
[ January 24, 2005, 02:38 PM: Message edited by: roger ]