Re: emt conduit installation
I hope I don?t step on any toes. I thought I would give a stab at this. It has been a while since I have done this. This is for my own edification.
Table 5, Chapter 9
3-- # 2 THHN @ .1158 = .3474 in2
4-- # 6 THHN @ .0507 = .2028 in2
3-- # 10 THHN @ .0211 = .0633 in2
I come up with .6135 in2
Table 4, Chapter 9
Over 2 @ 40% -- 1 1/2 EMT @ .814 in2
I would like to take this one step further, what about ?derating? (adjustment factor, Table 310.15(B)(2)(a)) for this situation? I would think without knowing the # of Current Carrying Conductors we could not get a good answer. Is this correct?
Norb