IMO, yes. EMT needs to be supported per 358.30.If EMT conduit is used to run data, phone wiring, does it need to comply with 3 feet support from a J-box?
But does Article 725 require a Chapter 3 compliant raceway, or even require that any sleeve for the cables be in the form of a Chapter 3 compliant raceway? If not, I don't see any prohibition on using some parts that could be made into a Chapter 3 compliant raceway in a laxer fashion as a sleeve for the Article 725 cables.Nothing in Article 725 says you are not required to comply with the raceway installation rules found in Chapter 3, so all of the rules for the installation of EMT apply.
If the install is made using a raceway system, the raceway system must be installed per the Chapter 3 rules, even where the wiring within the raceway system is not required to be in a raceway system.But does Article 725 require a Chapter 3 compliant raceway, or even require that any sleeve for the cables be in the form of a Chapter 3 compliant raceway? If not, I don't see any prohibition on using some parts that could be made into a Chapter 3 compliant raceway in a laxer fashion as a sleeve for the Article 725 cables.
Basically, if the install would be compliant if the EMT magically disappeared, I don't see how the presence of the EMT can make it non-compliant.
Cheers, Wayne
Great. So whenever a raceway isn't required, we can just call an "almost" raceway system a sleeve.If the install is made using a raceway . . .
If you are just installing sleeves, then that is not really subject to any rules.
That would be a typical distinction.Wayne would a raceway be box to box?
And a sleeve just that?
If the raceway is connected box to box, it will get a red tag from me if the raceway was not installed in accordance with the rules in Chapter 3.That would be a typical distinction.
But if the install would be compliant with cardboard boxes and string and chewing gum, and you choose to use metal boxes and sticks of EMT to give a higher quality install, I don't see why you need to comply with all the raceway rules, as you didn't need a raceway in the first place. So in that case only let's just call anything less than a fully compliant raceway system a "sleeve" or "extra, optional protection".
Cheers, Wayne
The flip side of that statement is that if we further omit the two box connectors at each end of the EMT, now it's suddenly OK for Article 725 installations that don't require raceways or boxes? That makes no sense.If the raceway is connected box to box, it will get a red tag from me if the raceway was not installed in accordance with the rules in Chapter 3.
It does not make any sense and given that the support requirements are there not only to help protect the wiring inside, but also to protect people below the raceway, especially firefighters pulling ceilings under fire conditions.The flip side of that statement is that if we further omit the two box connectors at each end of the EMT, now it's suddenly OK for Article 725 installations that don't require raceways or boxes? That makes no sense.
When boxes and raceways aren't required, they are just decorations. As long as they don't damage the cable, or otherwise interfere with any of the requirements for installing that cable, they can't cause an NEC violation.
Of course, for the OP, the job specs may have something to say on the matter.
Cheers, Wayne
There's always 110.12 when you really need it....
Probably needs to go on a 2029 PI list...any raceway installed in lengths exceeding 10', even where used only as a sleeve shall be supported in accordance with the raceway article.
I agree with Wayne here. Consider that the "raceway" is not even used for anything covered by the NEC. Say I use it to run an air line through. Does the EMT still have to meet the 358 requirements? I think that is obviously a no, so what is the distinction between that and something that is covered in the NEC but that does not require a raceway?It does not make any sense and given that the support requirements are there not only to help protect the wiring inside, but also to protect people below the raceway, especially firefighters pulling ceilings under fire conditions.