EMT connector Bushing

Status
Not open for further replies.

tterayama

New member
Manufacturer's publications do not indicate if bushings are required. Do these fittings have sufficient rounded edges to prevent abrasion?
 
IMO no. You'll need a bushing with an insulated throat or a bushing installed on the threads if the conductors are #4 AWG or larger.

Welcome to the forum. :)
 
Last edited:
Pb's are cheap insurance. They're made so cheaply now, some of them are razor sharp. We used some a while back(3/4") that were skinning the insulation so well off the side of the wire you'd of thought it was done with a knife!:mad:
 