PVC male adapters have the sharpest throats I've seen, next to un-reamed rigid.
Nothing defining "how smooth" is required. Some are much smoother than others.I agree that the new wording with the addition of item (2) is terrible for the reason that you noted. I'm guessing that someone thought that an EMT connector does not meet the smoothly rounded edges part.
The product standard defines what is required for a listed fitting.Nothing defining "how smooth" is required. Some are much smoother than others.
I was referring to when NEC says smooth they don't have any real guide for what is smooth enough. There are some fittings that have relatively smooth edges and some that will easily skin conductors during pulling operations, and there is some chance you can get smoother edges on RMC than some those fittings at times, yet RMC always requires a separate bushing fitting.The product standard defines what is required for a listed fitting.