I have to say we make a mountain out of a mole hill here.
All the EMT fittings are listed for grounding. If your not comfortable with using fittings as the grounding path then pull a wire EGC. :smile:
All this talk about surface area etc, have any of you noticed what grounding methods actually pass UL testing?
Think of the ground whip on some light fixtures, or the Tek screwed foot lug in an HVAC unit. Or that I can use a 10 AWG as the grounding means for up to 60 amps. Or the fact that with a 'self grounding' receptacle the grounding path may be just the 6-32 screw and a very small spring steel clip wedges against it. Or the fact that 'Wagos' are suitable for grounding. Or that 'grounding clips' are acceptable.
My point is there are many ways to get it done, each one of us looks at it differently.
It is my opinion that if EMT was not providing good grounding results in the field the NEC would have changed the rules, each year people ask them to and it is rejected for lack of facts.
Here is the most recent panel statement to explain the rejection of 3 proposals asking for a 'wire' EGC.