CGY44
Member
- Location
- Black Hawk SD
is there a emt fitting listed for damp locations, and if not what does everyone use in a Damp location?
thank you
thank you
infinity said:I'm guessing but I think that a standard set screw EMT connector or coupling would be OK in a damp location.
LJSMITH1 In the fittings industry said:These statements seem to conflict with each other. The first says a "raintight fitting" can't be used outside, which is a wet location per the NEC, and the second says that a raintight fitting is tested with method that simulates rain.
As a side note, do you know if threaded rigid conduit couplings are tested to this standard? Threaded rigid couplings leak much more than the "old" type (before UL changed the rules to require better sealing) of compression EMT fittings.
Location, Wet. Installations under ground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
Look on the fitting box it should be listed there.CGY44 said:is there a emt fitting listed for damp locations, and if not what does everyone use in a Damp location?
thank you
LJSMITH1 said:"Wet" and "Damp" are terms that are commonly interchanged in the field. However, in the literal sense, a Wet location is an application in direct contact with the earth, or in a location subject to saturation with a liquid. Damp locations are those areas not subjected to saturation, but moderate degrees of moisture.
In the fittings industry, "Raintight" means that the fitting is suitable for a damp location. "Liquidtight" means that the fitting is suitable for a wet location.
A setscrew or standard compression fitting is not considered a wet or damp location fitting, it is considered "dry". However a dry location is defined in NEC Art. 100 as "A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction."
UL514B requires raintight fittings to be sprayed with water for 1 hour using a special test fixture, with a specific volume of water, through calibrated spray heads. The fittings pass if no water enters the conduit/fitting area. Liquidtight fittings have a similar test, however the medium is oil, and the test is for 30 minutes.
So to answer your question, Raintight fittings are the best choice for a damp environment. You can use Bridgeport's 250-RT2 series fittings. They have an integral seal that works well in this type of environment.
Refresh my memory. If I'm using a THHN/THWN conductor where does the NEC state I have to use a certian fitting?don_resqcapt19 said:The first says a "raintight fitting" can't be used outside, which is a wet location per the NEC, and the second says that a raintight fitting is tested with method that simulates rain.
chris kennedy said:Refresh my memory. If I'm using a THHN/THWN conductor where does the NEC state I have to use a certian fitting?
I was just trying to ruffle some feathers. I'll spin the CD if it has some tunes I haven't heard yet.cadpoint said:The underlining thought is your making a complete mechanical application to the correct enviroment, its in the book, gezz spin the CD... :roll:
chris kennedy said:Refresh my memory. If I'm using a THHN/THWN conductor where does the NEC state I have to use a certian fitting?
realolman said:Is it OK to put pipe dope on rigid threaded couplings?
[IMG said:http://www.bptfittings.com/images/products/250-RT2-02.jpg[/IMG]
infinity said:Nothing like a bit of free advertising for Bridgeport fittings.
don_resqcapt19 said:These statements seem to conflict with each other. The first says a "raintight fitting" can't be used outside, which is a wet location per the NEC, and the second says that a raintight fitting is tested with method that simulates rain.
As a side note, do you know if threaded rigid conduit couplings are tested to this standard? Threaded rigid couplings leak much more than the "old" type (before UL changed the rules to require better sealing) of compression EMT fittings.
6.3.2.1 A liquid-tight FITTING shall comply with the oil spray test described in Clause 8.16.6 or 8.18.4. A
LIQUID-TIGHT FITTING is usable in wet locations and is also rain-tight and concrete-tight.