Sierrasparky said:How long have the emt fittings been around with the plastic seal? My local supply house still does not get these. I had to go outside my area to get them.
Anyone have any trouble using these. Even on a factory end they seem to take a bit of finess to fully seat the conduit.
We have been producing these since 2003 - ever since UL changed the requirements for compression type fittings.
As for the fitting assembly, the end of the conduit should be cut with a tubing cutter and have no burr. The tubing cutter should not distort the conduit OD so much as to cause a problem inserting it into a preassembled fitting. Due to the tolerance swings with some manufacturers emt, sometimes the fitting needs to be disassembled to place each piece onto the conduit separately (i.e. Nut, compression ring, seal, then body). While the fitting is designed to work best with the nominal OD of a trade size, an OD at the max may be required to be assembled separately.