yep #12 two wires 277v going to hang 99 high bay fluorescent fixtures on 10ft of jack chain figured 7 circuitsWhat about wire and all
no there will be nine rows of 230 ft 20ft apart i am going to run one 1inch conduit to connect all 9 rows
thats for conduit only? Thanks for replyI'd like to add a day (now 4) to my initial estimate. I'm assuming 3 men per day. 3*8*4= 96
(I hope I'm not too optimistic).
Thanksto run the conduit 157 hours this does not include the fixtures or wire give me more information hours and material for the rest
thats for conduit only? Thanks for reply
yep #12 two wires 277v going to hang 99 high bay fluorescent fixtures on 10ft of jack chain figured 7 circuits
no there will be nine rows of 230 ft 20ft apart i am going to run one 1inch conduit to connect all 9 rows
no there will be nine rows of 230 ft 20ft apart i am going to run one 1inch conduit to connect all 9 rows
Presuming 3-ph power, I'd suggest nine circuits with 11 fixtures per.yep #12 two wires 277v going to hang 99 high bay fluorescent fixtures on 10ft of jack chain figured 7 circuits
home run will be #10 furthest row 11x280ballast watts*277=11.1a was going to increase fixture count per circuit as they got closer to cb but IHow far away will the furthest 230 ft row be from the OCPD in the panel?
If 200 ft away with a 16 amp load 2 x 12.9 x 16 x 200 / CM #12 6530 = 12.64 VD. 277 x 3% = 8.3 Volts allowed. # 12 is too small.
Or find needed wire size CM = 2 x 12.9 x 200 x 16 / 8.3 = 9946 CM #10
2 = single phase (three phase system but single phase load.)
12.9 = K value for copper
200 = distance
16 = current on circuit (Assumed load on each circuit.)
8.3 = voltage drop allowed 277 x 3%
This math is only for the home runs. Does not include the length for the rows of lights. Just to show why I don't believe the #12 wire would be large enough. More info would be needed to do the complete circuit VD calculation.
21019 A 1 FPN 4. I know FPN's are not enforceable but this is a good rule. You wouldn't want premature failure or lamps and ballasts due to under voltage.
Please correct me if I missed something.
Thanks again I would not have put that many hours on it and of course got burnt that is why I asked dipping into commercial slowly a lot more codes to study after work what fun resi is slow so gotta surviveYes, conduit only. It's all about the planning.
home run will be #10 furthest row 11x280ballast watts*277=11.1a was going to increase fixture count per circuit as they got closer to cb but I
will use #10 wire as you suggested no headaches later fixtures are 120-277v
after research not comfortable with 12 will use 10cuKeep in mind once you go over 9 ccc in a raceway with #12 THHN you can no longer terminate those wires on a 20 amp OCPD.
Thanks again I would not have put that many hours on it and of course got burnt that is why I asked dipping into commercial slowly a lot more codes to study after work what fun resi is slow so gotta survive![]()