Is EMT ever permitted in wet locations? Even with rain tight fittings it is just damp locations, correct? Code references too please.
Thank-you
Thank-you
take a look at 358.10.
You can bury emt-- I wouldn't but I have seen it done
The 2" emt RT are about $1.00 more than the compression ones however the 1/2" emt rt are a bit more than double the cost of the compression--.92 as opposed to .41. Not so bad unless you have lots of themAre raintight / wet fittings significantly more expensive than "regular"?
I've seen it too: ERT conduit (electrical rust tubing).You can bury emt-- I wouldn't but I have seen it done
NYC has amendment that prohibits emt underground and outdoor wet locations. For rain tight couplings I would have to travel to Pennsylvania. Nobody stocks them here.
Were would you use the RT EMT fittings, since the amendment that EMT is prohibited? Just asking.
I still don't understand the requirement of rain tight fittings when the installed conductor is THHN/THWN.
IMO, there was nothing wrong with the regular compression fittings.
I still don't understand the requirement of rain tight fittings when the installed conductor is THHN/THWN.
IMO, there was nothing wrong with the regular compression fittings.
Compression fittings are not RT and the idea is to inhibit water in the conduit. Why not use set screw connectors for that matter
I agree...threaded couplings leak a lot more than standard compression couplings and the code requires that raceways be arranged to drain, so there was no need to make a change in the type of coupling required for wet location EMT.I agree. I can't see regular compression fittings being any worse than the straight threaded rigid couplings that ARE allowed outside.
I agree...threaded couplings leak a lot more than standard compression couplings and the code requires that raceways be arranged to drain, so there was no need to make a change in the type of coupling required for wet location EMT.
I agree...threaded couplings leak a lot more than standard compression couplings and the code requires that raceways be arranged to drain, so there was no need to make a change in the type of coupling required for wet location EMT.
I agree...threaded couplings leak a lot more than standard compression couplings and the code requires that raceways be arranged to drain, so there was no need to make a change in the type of coupling required for wet location EMT.
Not so much the equipment you use as it is how you route the raceway. Do not run it so there are low spots for water to accumulate, if you have to have a low spot try to place an enclosure in that low spot and provide weep holes in the bottom of that enclosure. Some will argue drilling weep holes in some items violates listing - and that can be a concern - and especially in some conditions, weep hole in explosion proof enclosure would definitely not be good - but they make drain fittings for such areas, you need an additional hub on the bottom of the enclosure to insttall it in.I have never seen this done and don't know what equipment I would use.
Anyone have any pictures?
Yes it is his opinion, I totally agree with him though.This is your opinion not code, correct? Just want to make sure others understand
This is your opinion not code, correct? Just want to make sure others understand