Can anyone tell me if and where the NEC forbids running EMT in the top groove of the underside of corregated metal sheet roofing. I know new jersey inspectors have failed jobs recently. Is it in the NEC? Thanks
raider1 said:There is a new 2008 NEC code section that prohibits this. Take a look at 300.4(E). Here is what this section says:
(E) Cables and Raceways Installed Under Roof Decking. A cable- or raceway-type wiring method, installed in exposed or concealed locations under metal-corrugated sheet roof decking, shall be installed and supported so the nearest outside surface of the cable or raceway is not less than 38 mm (1? in.) from the nearest surface of the roof decking.
FPN: Roof decking material is often repaired or replaced after the initial raceway or cabling and roofing installation and may be penetrated by the screws or other mechanical devices designed to provide “hold down” strength of the waterproof membrane or roof insulating material.
Exception: Rigid metal conduit and intermediate metal conduit shall not be required to comply with 300.4(E).
Chris
I couldn't picture what they were talking aboutJohnJ0906 said:
JohnJ0906 said:
sevlander said:Thanks,I knew it had come up before, just couldn't figure out where.
N.J. has not yet adopted 2008,but I think inspectors are already looking at this.