358.12 is Uses not permitted for EMT.
(3) In cinder concrete or cinder fill where subject to permanent
moisture unless protected on all sides by a layer of
noncinder concrete at least 50 mm (2 in.) thick or unless
the tubing is at least 450 mm (18 in.) under the fill.
Not sure what you mean. Maybe its a northeast thing but I was always taught the cinders in cinderblock eats away at EMT and it deteriorates. I wasn't sure if it was an actual code or just trade knowledge
cinder block
noun
: a block that is made of cement and coal cinders and that is used in building
Indeed.Key word here is "in" not on the surface
Thanks... The moisture on the block is enough to eat it away. I've seen it. Wasn't sure of the code.Indeed.
OP, there is a thing in the masonry world called efflorescence that can damage galvanized metal but NEC does not do anything special to mitigate any damage cause by it. There has to be water present for efflorescence to be an issue.
I live in the former coal capital of the universe. All the old buildings are CinderblockI am in the Northeast and have never heard this.
Perhaps an issue with true 'cider block' but most blocks being installed today are not cinder, they are concrete blocks.
Thanks... The moisture on the block is enough to eat it away. I've seen it. Wasn't sure of the code.
Sent from my LG-D851 using Tapatalk
I am in the Northeast and have never heard this.
Perhaps an issue with true 'cider block' but most blocks being installed today are not cinder, they are concrete blocks.
I'm not talking about new construction talking about old buildings. I wire where are you locatedIwire has something here a CMU concrete masonry Unit does not have coal cinders in its composition.
Nohas it been painted 30 -40 times and have a thick coat of paint?
. Iwire where are you located