Emt on cinderblock

Status
Not open for further replies.
Thanks... The moisture on the block is enough to eat it away. I've seen it. Wasn't sure of the code.

Sent from my LG-D851 using Tapatalk
That moisture is usually only a problem in basements - but not necessarily all basements. Moisture may still be a problem if not true cinder in the concrete but the cinder presence will make it worse. I see a lot of corrosive effects on most any masonry surface that remains damp most of the time.

I'm in NePa and never heard of it, nor when I was from Philly. But if it is an issue use mineralacs.
Those are galvanized as well. Just takes longer as the clamps need to deteriorate first then the raceway can get started;)
 
Reminds of of a product from Arlington. These are great. Quick to install and easy to use. I don't think I would use them outdoors though.

View attachment 13130

I would use them for some types of installation EMT inside might be one I would use them for but those things are also listed for RMC.

The parking garage at my local mall had those holding all the RMC on the ceilings and walls, I would bet less than 1% are not broken. Now the boxes are supporting the conduits. :happysad:
 
I would use them for some types of installation EMT inside might be one I would use them for but those things are also listed for RMC.

The parking garage at my local mall had those holding all the RMC on the ceilings and walls, I would bet less than 1% are not broken. Now the boxes are supporting the conduits. :happysad:
Steel version of the clamp may not break, but in the parking garage situation you may want more then a simple wedge anchor to mount it with.
 
This technique is used in the oil field industry especially with sandridge answer tri state electrical in North Oklahoma rigid conduit is strapped on top of the concrete blocke

Sent from my SM-G900V using Tapatalk
 
I would use them for some types of installation EMT inside might be one I would use them for but those things are also listed for RMC.

The parking garage at my local mall had those holding all the RMC on the ceilings and walls, I would bet less than 1% are not broken. Now the boxes are supporting the conduits. :happysad:
I'm pretty sure they are listed for emt too.

I would not even consider them for a parking garage. You need stuff that's more than bullet proof to survive in that environment.
 