How long has the EMT requirement been in place for houses in Chicago? Are there any houses in the city that were wired with NM cable? Does this apply to the suburbs or just the city itself?
Do they sell NM cable and accessories in big box stores in those areas that require metal conduits?My understanding is the Chicago Electrical Code area extends just to Cook county. The suburbs in the neighboring counties, like Lake, follow the NEC instead.
Chicago does not update their code on a regular basis. I believe they had their previous code edition for almost 20 years.Speaking of Chicago, it was my understanding that they have a rule that prohibits outside service disconnects. They gonna write this out of the 2020 edition for homes?
The Chicago Electrical Code only applies to Chicago itself, however many of the suburbs in the area, including ones outside of Cook County require EMT for dwelling units.My understanding is the Chicago Electrical Code area extends just to Cook county. The suburbs in the neighboring counties, like Lake, follow the NEC instead.
Their rule in 230.70(A) for the 2018 Chicago Electrical Code says:Speaking of Chicago, it was my understanding that they have a rule that prohibits outside service disconnects. They gonna write this out of the 2020 edition for homes?
I am not sure when they will make another update. There was around 20 years between the current one and the previous one.(1) One- and Two-Family Dwellings. In one- and two-family dwellings the service disconnecting means shall be installed at a readily accessible location in the basement or first floor of the building at a point not exceeding 1.52 m (5 ft) from the point of entry into the building. When the length of the service raceway exceeds 1.52 m (5 ft) from the point of entry into the building, the service raceway shall conform to the requirements of 230.6.
When did EMT come out? That is a relatively newer product correct? 60's?
I have some recollection of EMT coming in mid century, I guess I am mistaken. I don't recall seeing EMT in any installations older than early 60's.EMT originated in the '60's?!?!!? More like the '20s. In the 1928 NEC, EMT is Article 508.
I don't think it was ever an actual rule in Rockford. But some of the inspectors claimed it was and would tell homeowners that when they applied for permits. Just another reason to avoid permits.Some other bigger Illinois cities (such as Rockford) adopted the no rope rule at one point, but later rescinded it.
Do they sell NM cable and accessories in big box stores in those areas that require metal conduits?
I don't think it was ever an actual rule in Rockford. But some of the inspectors claimed it was and would tell homeowners that when they applied for permits. Just another reason to avoid permits.
Bump.How is EMT run in wood framed single family homes? Seems like running horizontal through studs would be difficult. Is every outlet dropped from the attic? Are all houses built with open web beams between floors? No j-boxes would be allowed in this enclosed space so everything has to be up and down to outlets. How much does all this EMT add to the price of a house? Inquiring minds want to know.
I grew up in Miami-Dade county (Florida). Up until about the early 70s all residential was in EMT. This was part of the old South Florida Building Code which is now long gone. Since everybody piped most were pretty good and quick at piping in wood framing. In many walls you can notch to lay in the EMT. Since all our buildings were CBS on all exterior walls the EMT was strapped with "wrap" straps and cut nails so it would be just flush with furring strips. Back then the EMT was always used as the EGC. Piped houses are great when you want to do remodeling and alterations.How is EMT run in wood framed single family homes? Seems like running horizontal through studs would be difficult. Is every outlet dropped from the attic? Are all houses built with open web beams between floors? No j-boxes would be allowed in this enclosed space so everything has to be up and down to outlets. How much does all this EMT add to the price of a house? Inquiring minds want to know.