Since ceiling varies on height I assume I will have to
cut and thread RMC ??
looks like it. a thought.....
fixture mounts to a j box, right?
how about using two swivel covers, with
a nipple in between? at least it would be
a cleaner install. bolt the cover directly to
the fixture.....
now, so you don't have to take your general
liability policy for a spin, what i'd do, is use
#10 stranded for the ground, strip it and
bolt it to the upper j box with fender washers
and nuts and bolts, and bolt it the same way
toi the fixture, with fender washers.
then the #10 makes a pretty fair safety leash
as well as a bond.
and yeah, you are gonna have to cut and thread.
so, you are in two sticks of 1/2" grc, and 4 swivel
covers, per fixture, and the labor to cut and thread.
about $100 per fixture.....