i'm feeling stupid at the moment, but i'm assuming you are talking about combo truss with wood stringers
and thinwall tubing for the lattice.....:dunce:
i live in earthquake land, and pretty much everything here gets hung from the bottom stringer.
where you have an all steel truss, made of back to back angle iron for the stringers, with angle
iron at a 45 degree angle for the segments, dropping running thread from the lower one is the
norm.... and not trivial loads, either. half inch rod, and racks of 4" EMT, and a beam clamp is
what is used around here. the only time i've used the top, is if i throw a piece of unistrut across
the top of the truss, in the cavities of the robertson decking, to drop a rod in a specific place.
and i'll seldom use a beam clamp, just use square strut washers between the angles of the bottom
stringer, and put the rod in between them.
i've never had a do over in 40 years of this... :huh:
We call that "bar joist" construction back east. I've never understood people requiring supports from the top chord of the assembly. Mechanically the joist doesn't care if the load is on the top chord or bottom chord. The only thing I can think of that might be an issue is if the load set up a bending moment perpendicular to the long axis of the joist. Most joists I'v seen of this type are structurally attached at the top chord, and it might (emphasize "might") make a difference then.